Which loads are 40-ampere and 50-ampere branch circuits permitted to supply in any occupancy?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4086
- D: Cooking appliances fastened in place
Explanation
210.23 permits 40- and 50-ampere branch circuits to supply cooking appliances that are fastened in place in any occupancy. In other than dwelling units they may also supply fixed lighting with heavy-duty lampholders, infrared heating units or other utilization equipment.
More questions: Branch Circuits, GFCI and AFCI
- 4087In a dwelling unit, a 30-ampere branch circuit is permitted to supply which of the following?
- 4088A branch circuit supplies a continuous load of 16 amperes and no noncontinuous load. What is the minimum conductor ampacity before any adjustment or correction?
- 4089A branch circuit supplies 24 amperes of continuous load and 6 amperes of noncontinuous load. What is the minimum standard overcurrent device rating?
- 4090For branch circuit sizing, a continuous load is one where the maximum current is expected to continue for how long?
- 4091When may a branch circuit overcurrent device be sized at 100 percent of the continuous load instead of 125 percent?
- 4094A multiwire branch circuit supplies receptacles in a dwelling. What does the NEC require at the point where the branch circuit originates?