A ground rod measured 40 ohms, so a second rod was driven 6 ft away. The pair still measures 30 ohms. What else is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5013
- A: Nothing further is required by the Code
Explanation
Once the single rod is supplemented by a properly spaced additional electrode, the Code does not require further electrodes even if 25 ohms is not reached. See 250.53.