Question 5014 of 844 · Washington 01 Journey Level Electrician Exam
Which of the following is NOT permitted to be used as a grounding electrode?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5014
- B: Metal underground gas piping
Explanation
Metal underground gas piping systems are specifically prohibited as grounding electrodes. The other items are recognized electrodes. See 250.52(B).