Question 6041 of 844 · Washington 01 Journey Level Electrician Exam
In a box fill calculation, a single receptacle on one yoke counts as
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6041
- A: Two conductor volumes based on the largest conductor connected to it
Explanation
Each yoke or strap containing one or more devices counts as two volume allowances based on the largest conductor connected to the device. See 314.16(B).