Two equipment grounding conductors enter a box. How are they counted for box fill?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6042
- B: As a single volume allowance
Explanation
One or more EGCs entering a box are counted as a single volume allowance based on the largest EGC. Additional allowances apply only where many EGCs enter. See 314.16(B).