Question 6066 of 844 · Washington 01 Journey Level Electrician Exam
Which location permits Type NM cable?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6066
- B: Exposed and concealed work in normally dry locations
Explanation
NM cable is permitted in normally dry locations in one- and two-family dwellings and other permitted occupancies. It may not be used as service-entrance cable, embedded in masonry or concrete, or in wet or damp locations. See 334.10 and 334.12.
More questions: Wiring Methods, Conductors and Boxes
- 6067In an attic reached only by a scuttle hole, NM cable run across the top of joists must be protected by guard strips within what distance of the scuttle hole?
- 6068In an unfinished basement, NM cable run at angles to joists must be run through bored holes or on running boards if it is smaller than
- 6069The ampacity of NM cable conductors is generally determined using which temperature column?
- 6070Which is a permitted use of Type UF cable?
- 6071Where rigid PVC conduit is exposed above grade and subject to physical damage, it must be
- 6001What is the minimum cover for direct burial cable under the general condition (not under a building, slab, or roadway), 600 V or less?