In an attic reached only by a scuttle hole, NM cable run across the top of joists must be protected by guard strips within what distance of the scuttle hole?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6067
- C: 6 ft
Explanation
In attics without permanent stairs or ladders, protection by guard strips is required only within 6 ft of the nearest edge of the scuttle hole or attic entrance. See 334.23 and 320.23.