Question 7009 of 966 · Washington 01 Journey Level Electrician Exam

Grounding-type receptacles are installed downstream of a GFCI on a circuit that has no equipment grounding conductor. How must they be marked?

Exactly one answer is correct.

Show solution

Correct answer to question 7009

  • D: GFCI Protected and No Equipment Ground

Explanation

Under 406.4(D)(2)(c) (406.12(D) in NEC 2026), grounding-type receptacles supplied through a GFCI may replace nongrounding ones, but each must be marked GFCI Protected and No Equipment Ground. No equipment grounding conductor may be connected between these receptacles.

Next to question ›