May a receptacle be installed face up in a kitchen countertop?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7012
- B: Only if the receptacle assembly is listed for countertop or work surface use
Explanation
Section 406.5(G)(1) (406.14 in NEC 2026) prohibits receptacles installed face up in countertops or similar work surfaces unless the receptacle assembly is listed for that application. Spilled liquids can otherwise enter the contacts. Pop-up assemblies listed for countertops are the usual solution.