Question 7032 of 844 · Washington 01 Journey Level Electrician Exam
The old limit of 42 overcurrent devices for lighting and appliance branch-circuit panelboards was removed in the 2008 NEC. What limits the number of devices today?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7032
- B: The number the panelboard is designed and listed for
Explanation
Since the 2008 NEC dropped the 42-circuit limit, 408.54 simply requires panelboards to prevent installing more overcurrent devices than the number for which they are designed, rated and listed. The manufacturer sets that number.
More questions: Equipment, Devices and Luminaires
- 7033A plug-in circuit breaker is back-fed to supply a panelboard. How must it be installed?
- 7034What is the maximum rating of the overcurrent device protecting a panelboard?
- 7035In a commercial building, a panelboard is supplied by a feeder from another panel. What must the panelboard be marked with?
- 7036In a panelboard supplied by a 4-wire delta system with a high leg, which phase position must the high leg occupy?
- 7037In a dwelling unit, where are overcurrent devices such as a panelboard not permitted?
- 7038Which type of luminaire is not permitted in a clothes closet?