Question 7056 of 844 · Washington 01 Journey Level Electrician Exam
What does Article 424 require for fixed electric space-heating equipment?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7056
- C: A means to disconnect the heater and its controls from all ungrounded conductors at once
Explanation
Section 424.19 requires means to disconnect the heater and its associated equipment from all ungrounded conductors at the same time. Where the heater is supplied by more than one source, the disconnects must be grouped and marked.