A permanently connected appliance rated above 300 VA is not within sight of its branch-circuit breaker. What is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7053
- D: The breaker must be lockable open with a permanent locking provision
Explanation
Section 422.31(B) allows the branch-circuit switch or breaker as the disconnect if it is within sight of the appliance or can be locked in the open position. The locking provision must stay in place whether or not the lock is installed.
More questions: Equipment, Devices and Luminaires
- 7056What does Article 424 require for fixed electric space-heating equipment?
- 7058Which use of flexible cord is not permitted?
- 7059A flexible cord is run from one room to another through a hole in the wall. Is this permitted?
- 7060How must a flexible cord be connected so that tension is not transmitted to joints or terminal screws?
- 7061Equipment operating at 120/240 volts has exposed live parts on one side and no live or grounded parts on the other side of the working space (Condition 1). What is the minimum working space depth?
- 7062A 480Y/277 volt panelboard faces a concrete wall across the working space (Condition 2). What is the minimum working space depth?