A permanently connected appliance is rated 250 VA. What may serve as its disconnecting means?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7052
- B: The branch-circuit overcurrent device
Explanation
Section 422.31(A) permits the branch-circuit overcurrent device to serve as the disconnect for permanently connected appliances rated 300 VA or 1/8 hp or less. Larger appliances need a disconnect that meets 422.31(B).