Electric baseboard heaters are usually installed below receptacle outlets. What does Article 424 say about this?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7057
- D: Heaters should not be below receptacle outlets unless their instructions allow it
Explanation
Section 424.9 covers receptacle outlets built into baseboard heaters, which may not be wired to the heater circuit. Its informational note points out that listed baseboard heaters come with instructions that prohibit installing them below receptacle outlets unless the instructions allow it. Cords hanging over a heater could overheat.
More questions: Equipment, Devices and Luminaires
- 7058Which use of flexible cord is not permitted?
- 7059A flexible cord is run from one room to another through a hole in the wall. Is this permitted?
- 7060How must a flexible cord be connected so that tension is not transmitted to joints or terminal screws?
- 7061Equipment operating at 120/240 volts has exposed live parts on one side and no live or grounded parts on the other side of the working space (Condition 1). What is the minimum working space depth?
- 7062A 480Y/277 volt panelboard faces a concrete wall across the working space (Condition 2). What is the minimum working space depth?
- 7063Two 480 volt switchboards with exposed live parts face each other across an aisle (Condition 3). What is the minimum working space depth?