Question 7069 of 844 · Washington 01 Journey Level Electrician Exam
Under the 2020 and 2023 NEC, which equipment must receive a field-applied arc flash warning marking?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7069
- B: Panelboards and similar equipment in other than dwelling units likely to need servicing while energized
Explanation
Section 110.16(A) requires switchboards, switchgear, enclosed panelboards, industrial control panels, meter socket enclosures and motor control centers in other than dwelling units to be marked to warn of arc flash hazards where examination or maintenance while energized is likely. The marking must be clearly visible before work begins.
More questions: Equipment, Devices and Luminaires
- 7015In a new dwelling, a switch box for a bedroom lighting switch is fed with cable. What does the code generally require in that box?
- 7016Which condition allows a lighting switch box to be installed without a grounded conductor under 404.2(C)?
- 7017When may a switch disconnect the grounded conductor of a circuit?
- 7018Three-way and four-way switches must be wired so that switching is done in which conductor?
- 7019How must snap switches, including dimmers, be grounded?