A motor with a service factor of 1.0 has a nameplate current of 20 A. What is the maximum separate overload setting under 430.32(A)(1)?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8008
- A: 23 A
Explanation
With a service factor of 1.0, the overload may not exceed 115 percent of nameplate current. 20 A times 1.15 equals 23 A. 25 A would apply only to motors with a 1.15 service factor.