Question 8026 of 1033 · Washington 01 Journey Level Electrician Exam
A portable motor is cord-and-plug connected. What may serve as its disconnecting means?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8026
- D: The attachment plug and receptacle
Explanation
Section 430.109(F) allows a horsepower-rated attachment plug and receptacle as the disconnect for cord-and-plug connected motors. Unplugging the cord removes all power.
More questions: Motors, HVAC, Generators and Transformers
- 8027What is the minimum rating of a motor controller?
- 8028Where must the disconnecting means for a motor control circuit be arranged?
- 8029A motor control circuit has one side grounded. How must the circuit be arranged?
- 8032What does the code letter on a motor nameplate indicate?
- 8033A motor is connected wye-start, delta-run. Conductors between the controller and the motor are selected at what portion of the full-load current?
- 8034Feeder conductors supplying several motors must have an ampacity of at least what?