Where must the disconnecting means for a motor control circuit be arranged?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8028
- B: So that opening it disconnects the control circuit from all sources of supply
Explanation
Section 430.75(A) requires motor control circuits to be arranged so they are disconnected from all sources of supply when the disconnecting means is open. A separate control source must be disconnected along with the power circuit.