The largest motor on a feeder has a 100 A branch-circuit breaker. The other motors have FLCs of 20 A and 10 A. What is the maximum standard feeder breaker size?

Exactly one answer is correct.

Show solution

Correct answer to question 8037

  • B: 125 A

Explanation

Section 430.62(A) gives 100 A plus 20 A plus 10 A, which is 130 A. The feeder device may not exceed this value, so the next lower standard size of 125 A is the maximum.