Question 8050 of 844 · Washington 01 Journey Level Electrician Exam
A room air conditioner shares a branch circuit with lighting outlets. What is its maximum rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8050
- A: 50 percent of the branch-circuit rating
Explanation
Section 440.62(C) limits the room air conditioner to 50 percent of the branch-circuit rating when lighting units or other appliances are also supplied. This leaves capacity for the other loads.