Question 8052 of 844 · Washington 01 Journey Level Electrician Exam

Conductors from generator terminals to the first overcurrent device must have an ampacity of at least what?

Exactly one answer is correct.

Show solution

Correct answer to question 8052

  • A: 115 percent of the generator nameplate current

Explanation

Section 445.13(A) requires conductors from the generator output terminals to the first distribution device containing overcurrent protection to have an ampacity of at least 115 percent of the nameplate current rating. Neutral conductors may be sized under 220.61 (120.61 in NEC 2026).