Question 8054 of 966 · Washington 01 Journey Level Electrician Exam
What must a generator other than a cord-and-plug connected portable generator be equipped with?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8054
- A: A lockable disconnect that separates the generator from the circuits it supplies
Explanation
Section 445.18 requires generators to have one or more disconnecting means that simultaneously open all ungrounded conductors and can be locked in the open position. Workers can then isolate the generator from the premises wiring.