Question 8068 of 844 · Washington 01 Journey Level Electrician Exam
A 75 kVA dry-type transformer is installed indoors. What is the minimum separation from combustible material without a fire-resistant barrier?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8068
- D: 12 in
Explanation
Section 450.21(A) requires dry-type transformers of 112.5 kVA or less installed indoors to have at least 12 in of separation from combustible material, unless a fire-resistant, heat-insulating barrier is used. Transformers of 1000 volts or less that are completely enclosed are exempt.
More questions: Motors, HVAC, Generators and Transformers
- 8072Oil-insulated transformers installed indoors are generally required to be installed in what?
- 8074Secondary conductors leave a transformer and do not exceed 10 ft in length. What may they terminate in without protection at the secondary terminals?
- 8075Capacitors rated 1000 volts or less must discharge their residual voltage to what level within what time after disconnection?
- 8076What is the minimum ampacity of conductors supplying a capacitor?
- 8078Why are capacitors installed in motor circuits in industrial plants?
- 8001Branch-circuit conductors supplying a single continuous-duty motor must have an ampacity of at least what percentage of the motor full-load current?