Question 8072 of 844 · Washington 01 Journey Level Electrician Exam
Oil-insulated transformers installed indoors are generally required to be installed in what?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8072
- A: A transformer vault
Explanation
Section 450.26 generally requires oil-insulated transformers installed indoors to be in a vault, with limited exceptions. Oil is flammable, so the vault confines a fire.