A continuous-duty motor has a table full-load current of 28 A. What is the minimum ampacity of its branch-circuit conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8002
- D: 35 A
Explanation
Section 430.22 requires 125 percent of the table full-load current. 28 A times 1.25 equals 35 A. 32.2 A would result from wrongly using 115 percent.