When sizing motor branch-circuit conductors and short-circuit protection for a general-purpose motor, which current must be used?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8003
- A: The full-load current from the NEC motor tables
Explanation
Section 430.6(A)(1) requires the table values (Tables 430.247 to 430.250) rather than the nameplate current for conductor ampacity and for short-circuit and ground-fault protection. The table values give a consistent, conservative basis.