Question 9013 of 966 · Washington 01 Journey Level Electrician Exam
Unless the sealing fitting is identified for a higher fill, the conductors in a Class I seal may occupy no more than what percentage of the cross-sectional area of rigid metal conduit of the same trade size?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9013
- B: 25 percent
Explanation
The cross-sectional area of conductors or optical fiber tubes in a seal is limited to 25 percent of the area of rigid metal conduit of the same trade size. The 40, 31, and 53 percent values are the general Chapter 9 conduit fill limits and do not apply to seals.
More questions: Special Occupancies
- 9014A rigid metal conduit run leaves a Class I, Division 1 location and enters an unclassified area. Within what distance of the boundary must the boundary seal be installed?
- 9015Threaded rigid metal conduit in a Class I, Division 1 location must be made up wrenchtight with at least how many fully engaged threads?
- 9016Which wiring method is generally permitted in a Class I, Division 1 location?
- 9017Flexibility is needed at a motor terminal box in a Class I, Division 1 location. Which method is acceptable?
- 9018Enclosures for equipment in a Class II, Division 1 location must generally be of what type?
- 9019What is the basic design principle of explosionproof equipment?