Question 10008 of 966 · Washington 01 Journey Level Electrician Exam
The disconnecting means for crane runway conductors must be of what type?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10008
- C: Readily accessible, operable from the ground or floor, and lockable open
Explanation
A disconnecting means for runway conductors must be readily accessible and operable from the ground or floor level, open all ungrounded conductors, and be lockable open. This lets personnel de-energize the crane before working on it.
More questions: Special Equipment, Pools, PV and EV
- 10009When may an information technology equipment room use the special provisions of Article 645?
- 10011Branch-circuit conductors supplying information technology equipment under Article 645 must have an ampacity of not less than what percentage of the total connected load?
- 10012What is the minimum horizontal distance from the inside wall of a permanently installed pool for a general purpose 125-volt receptacle?
- 10013125-volt, 15- and 20-ampere receptacles located within what distance of the inside walls of a pool require GFCI protection?
- 10014At a dwelling with a permanently installed pool, where must the required 125-volt, 15- or 20-ampere receptacle be located?
- 10016Over an outdoor pool, what is the minimum height of a luminaire or ceiling fan above the maximum water level?