Question 10011 of 844 · Washington 01 Journey Level Electrician Exam
Branch-circuit conductors supplying information technology equipment under Article 645 must have an ampacity of not less than what percentage of the total connected load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10011
- B: 125 percent
Explanation
Branch-circuit conductors supplying one or more units of ITE must have an ampacity not less than 125 percent of the total connected load. ITE typically runs continuously.
More questions: Special Equipment, Pools, PV and EV
- 10012What is the minimum horizontal distance from the inside wall of a permanently installed pool for a general purpose 125-volt receptacle?
- 10013125-volt, 15- and 20-ampere receptacles located within what distance of the inside walls of a pool require GFCI protection?
- 10014At a dwelling with a permanently installed pool, where must the required 125-volt, 15- or 20-ampere receptacle be located?
- 10016Over an outdoor pool, what is the minimum height of a luminaire or ceiling fan above the maximum water level?
- 10017In an indoor pool area, the minimum height for a luminaire over the pool may be reduced to what height if the luminaire is totally enclosed and GFCI protected?
- 10018Switching devices must be located at least how far horizontally from the inside walls of a pool, unless separated by a solid fence, wall, or permanent barrier?