Question 10018 of 844 · Washington 01 Journey Level Electrician Exam
Switching devices must be located at least how far horizontally from the inside walls of a pool, unless separated by a solid fence, wall, or permanent barrier?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10018
- A: 5 ft
Explanation
Switching devices must be at least 5 ft horizontally from the inside walls of a pool unless separated by a solid fence, wall, or other permanent barrier, or listed for use within 5 ft. This keeps a person standing in or at the edge of the pool from operating a switch with wet hands.