Question 10021 of 844 · Washington 01 Journey Level Electrician Exam
A branch circuit supplies an underwater pool luminaire operating above the low-voltage contact limit. What protection is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10021
- B: GFCI protection installed in the branch circuit
Explanation
Underwater luminaires operating at more than the low-voltage contact limit must be supplied through a GFCI so that no shock hazard exists during relamping or under ground-fault conditions. Relamping a wet-niche luminaire normally means pulling it onto the deck, so the GFCI also protects the person servicing it.
More questions: Special Equipment, Pools, PV and EV
- 10022For sinusoidal ac, the low-voltage contact limit used in Article 680 is how many volts RMS?
- 10025What is the minimum size of a solid copper equipotential bonding conductor for a permanently installed pool?
- 10027Perimeter surfaces around a pool must be bonded for what minimum horizontal distance beyond the inside walls?
- 10030For conductive pool shells, perimeter surface bonding must attach to the structural reinforcing steel or copper grid at a minimum of how many points?
- 10031Pool water must be bonded by a conductive surface in contact with the water of at least what area?
- 10032Metal parts such as fences or railings must be bonded when within what distance of the inside walls of a pool, unless separated by a permanent barrier?