Question 10012 of 844 · Washington 01 Journey Level Electrician Exam
What is the minimum horizontal distance from the inside wall of a permanently installed pool for a general purpose 125-volt receptacle?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10012
- A: 6 ft
Explanation
Receptacles are not permitted within 6 ft of the inside walls of a pool. Between 6 ft and 20 ft, 125-volt, 15- and 20-ampere receptacles require GFCI protection.