Question 10047 of 844 · Washington 01 Journey Level Electrician Exam
A single PV string has modules with an Isc of 10 amperes. What is the minimum conductor ampacity before adjustment and correction, applying both 125 percent factors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10047
- D: 15.6 amperes
Explanation
First the maximum current is 10 A x 1.25 = 12.5 A. Conductors must then carry 125 percent of that maximum current for continuous duty: 12.5 A x 1.25 = 15.6 A, which is the same as Isc x 1.56.
More questions: Special Equipment, Pools, PV and EV
- 10049Under PV rapid shutdown rules, conductors outside the array boundary must be reduced to no more than what voltage within 30 seconds of initiation?
- 10050For PV rapid shutdown, the array boundary is defined as what distance from the array in all directions?
- 10052For one- and two-family dwellings, where must the PV rapid shutdown initiation device be located?
- 10053A PV system has dc circuits operating at 80 volts or more between any two conductors. What protection is required?
- 10055A PV module has an open-circuit voltage (Voc) of 40 volts. Ten modules are connected in series, and the temperature correction factor for the lowest expected ambient temperature is 1.12. What is the maximum PV circuit voltage?
- 10056A PV module has a temperature-corrected Voc of 48 volts. What is the maximum number of modules that can be connected in series on a one- and two-family dwelling?