Question 10056 of 844 · Washington 01 Journey Level Electrician Exam
A PV module has a temperature-corrected Voc of 48 volts. What is the maximum number of modules that can be connected in series on a one- and two-family dwelling?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10056
- D: 12
Explanation
The dwelling limit is 600 volts. 600 V divided by 48 V per module equals 12.5, so a maximum of 12 whole modules can be connected in series. Rounding up to 13 would exceed the limit.
More questions: Special Equipment, Pools, PV and EV
- 10064What protection is required for receptacles installed for the connection of EV charging equipment?
- 10065An EVSE has a maximum load of 48 amperes. What is the minimum OCPD rating for the branch circuit supplying it?
- 10066An EVSE is rated 40 amperes continuous. What is the minimum OCPD rating for its branch circuit?
- 10067How must each outlet installed for EVSE be supplied?
- 10068Indoor EV charging equipment is listed as requiring ventilation. What does the NEC require?
- 10069In NEC 2020 and 2023, EVSE rated more than 60 amperes or more than 150 volts to ground requires a disconnecting means with which characteristics?