In NEC 2020 and 2023, EVSE rated more than 60 amperes or more than 150 volts to ground requires a disconnecting means with which characteristics?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10069
- D: Readily accessible and lockable open
Explanation
EVSE rated more than 60 amperes or more than 150 volts to ground must have a readily accessible disconnecting means that is lockable open. If remote, a plaque on the equipment must show its location.