Question 10066 of 844 · Washington 01 Journey Level Electrician Exam

An EVSE is rated 40 amperes continuous. What is the minimum OCPD rating for its branch circuit?

Exactly one answer is correct.

Show solution

Correct answer to question 10066

  • B: 50 amperes

Explanation

The branch-circuit OCPD must be at least 125 percent of the maximum load: 40 A x 1.25 = 50 A. 50 A is a standard OCPD size.

Next to question ›