Question 10052 of 844 · Washington 01 Journey Level Electrician Exam
For one- and two-family dwellings, where must the PV rapid shutdown initiation device be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10052
- D: At a readily accessible location outside the building
Explanation
For one- and two-family dwellings, the rapid shutdown initiation device must be at a readily accessible location outside the building. Firefighters can then activate it without entering the structure.
More questions: Special Equipment, Pools, PV and EV
- 10053A PV system has dc circuits operating at 80 volts or more between any two conductors. What protection is required?
- 10055A PV module has an open-circuit voltage (Voc) of 40 volts. Ten modules are connected in series, and the temperature correction factor for the lowest expected ambient temperature is 1.12. What is the maximum PV circuit voltage?
- 10056A PV module has a temperature-corrected Voc of 48 volts. What is the maximum number of modules that can be connected in series on a one- and two-family dwelling?
- 10064What protection is required for receptacles installed for the connection of EV charging equipment?
- 10065An EVSE has a maximum load of 48 amperes. What is the minimum OCPD rating for the branch circuit supplying it?
- 10066An EVSE is rated 40 amperes continuous. What is the minimum OCPD rating for its branch circuit?