A PV string has modules with an Isc of 8 amperes. What minimum OCPD rating is required if the circuit needs overcurrent protection, using both 125 percent factors and the next standard size?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10048
- A: 15 amperes
Explanation
Maximum current is 8 A x 1.25 = 10 A, and the OCPD must be rated at least 125 percent of that, which gives 12.5 A. The next standard OCPD size above 12.5 A is 15 A.