Question 10061 of 966 · Washington 01 Journey Level Electrician Exam
A PV interconnection made between the service meter and the service disconnecting means is what type of connection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10061
- C: A supply-side connection
Explanation
Connecting a power production source on the supply side of the service disconnecting means is a supply-side connection. Load-side connections are made at or downstream of the service disconnect and are subject to the busbar limits.