Question 1087 of 844 · Washington 01 Journey Level Electrician Exam
At the service, the connection between the grounded (neutral) conductor and the equipment grounding conductor is made by the:
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1087
- D: Main bonding jumper
Explanation
Article 100 defines the main bonding jumper as the connection between the grounded circuit conductor and the equipment grounding conductor at the service. At a separately derived system, the equivalent connection is the system bonding jumper.
More questions: Definitions, Theory and Plans
- 1088The circuit conductors between the final overcurrent device protecting the circuit and the outlets are called:
- 1089Conductors running from the service equipment to a subpanel that contains the final branch-circuit breakers are classified as:
- 1090Ampacity is defined in the NEC as the maximum current a conductor can carry continuously:
- 1091In the NEC, the term approved means:
- 1092Equipment that has a label, symbol or identifying mark of an organization acceptable to the AHJ that maintains periodic inspection of its production is described as:
- 1093Under the NEC, operation of equipment in excess of its normal full-load rating that would cause damaging overheating if it persisted is called: