Question 11039 of 1033 · Washington 01 Journey Level Electrician Exam
May nonconductive optical fiber cables occupy the same raceway as electric light and power conductors operating at 1000 volts or less?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11039
- B: Yes, they are permitted
Explanation
Nonconductive optical fiber cables may occupy the same cable tray or raceway with conductors for electric light, power, Class 1, or non-power-limited fire alarm circuits operating at 1000 volts or less. They carry no current and cannot be energized by contact.
More questions: Emergency, Limited Energy and Communications
- 11040What is the minimum size of the bonding conductor for a communications primary protector?
- 11041At one- and two-family dwellings, the bonding conductor for a communications primary protector should be as short as practicable and not longer than what length?
- 11042In NEC 2020 and 2023, which article covers communications circuits such as telephone wiring?
- 11044Where must the outer conductive shield of a CATV coaxial cable entering a building be grounded?
- 11045What is the minimum size of the bonding conductor for a CATV coaxial cable shield?
- 11046Which communications cable type is required in a vertical riser shaft between floors, unless a higher-rated type is used?