At one- and two-family dwellings, the bonding conductor for a communications primary protector should be as short as practicable and not longer than what length?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11041
- A: 20 ft
Explanation
At one- and two-family dwellings, the primary protector bonding conductor must not exceed 20 ft in length. If this is not possible, a separate electrode and bonding to the electrode system is required.