Where must the outer conductive shield of a CATV coaxial cable entering a building be grounded?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11044
- B: As close as practicable to the point of entrance
Explanation
The coaxial cable shield must be bonded to the building grounding system as close as practicable to the point of entrance or attachment. This minimizes voltage differences between systems during lightning or power faults.