May communications circuit conductors be installed in the same raceway with electric light and power conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11048
- D: No, they must be kept separate except where specifically permitted
Explanation
Communications wires and cables must not be placed in any raceway, compartment, outlet box, or junction box with electric light, power, Class 1, or non-power-limited fire alarm conductors, except where specifically allowed. Barriers or listed equipment can allow both inside one enclosure in some cases.