The bonding conductor from a communications primary protector at a building is normally connected to what?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11049
- A: The intersystem bonding termination
Explanation
The communications primary protector bonding conductor is normally connected to the intersystem bonding termination, which ties communications, CATV, and power grounding systems together at the service. Using a common bonding point limits voltage differences between systems during lightning surges or power faults.