Question 12021 of 844 · Washington 01 Journey Level Electrician Exam

Using the standard method under the NEC 2020/2023, what general lighting load must be included in the service calculation for a one-family dwelling with 2,400 ft2 of livable floor area?

Exactly one answer is correct.

Show solution

Correct answer to question 12021

  • A: 7,200 VA

Explanation

The dwelling unit load for general lighting and general-use receptacles is 3 VA per ft2 (Table 220.12 in 2020, 220.41 in 2023). 2,400 ft2 x 3 VA = 7,200 VA. Garages, open porches and unfinished spaces not adaptable for future use are not counted.