A 2,000 ft2 dwelling has the minimum two small-appliance circuits and one laundry circuit. Under the NEC 2020/2023 standard method, what is the demand load for general lighting, small-appliance and laundry loads combined?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12022
- B: 5,625 VA
Explanation
Lighting is 2,000 x 3 VA = 6,000 VA, plus 2 x 1,500 VA small-appliance and 1,500 VA laundry gives 10,500 VA (Table 220.12 in 2020, 220.41 in 2023, 220.52). Applying the dwelling demand factors (Table 220.42 in 2020, Table 220.45 in 2023): first 3,000 VA at 100 % plus 7,500 VA x 35 % = 5,625 VA.
More questions: Load Calculations
- 12023A 3,200 ft2 one-family dwelling has three 20 A small-appliance circuits and one laundry circuit. Under the NEC 2020/2023 standard method, what is the net demand load for these loads plus general lighting?
- 12024Under the NEC 2020/2023 standard method, what is the demand load for general lighting, two small-appliance circuits and one laundry circuit in a 4,500 ft2 dwelling?
- 12025Optional method (NEC 2020/2023): a 2,000 ft2 dwelling has two small-appliance circuits, one laundry circuit, a 12 kW range, a 5 kW dryer, a 1,200 VA dishwasher and a 4,500 W water heater. What is the calculated general load (heating and AC excluded)?
- 12026Optional method (NEC 2020/2023), 120/240 V service: 1,800 ft2 dwelling, two small-appliance and one laundry circuit, 11 kW range, 5.5 kW dryer, 1,000 VA dishwasher, 800 VA disposal, 4 kW water heater, 6,000 VA central AC and 8 kW central electric furnace. What is the calculated load in amperes?
- 12027Optional method (NEC 2020/2023): a 1,500 ft2 dwelling with two small-appliance and one laundry circuit, a 10 kW range, 5 kW dryer and 4.5 kW water heater has six separately controlled 2 kW baseboard heaters and a 4,000 VA AC unit. What is the total calculated load?
- 12032A dwelling has one electric dryer rated 3,800 W. What load must be used for it in the NEC 2020/2023 service calculation?