Question 1112 of 844 · Washington 01 Journey Level Electrician Exam
For service equipment and panelboards, the minimum headroom of the working space is generally:
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1112
- C: 6.5 feet or the height of the equipment, whichever is greater
Explanation
110.26(A)(3) requires the working space height to be at least 6.5 feet or the height of the equipment, whichever is greater. A dwelling exception covers small service equipment in existing units.