Question 12030 of 966 · Washington 01 Journey Level Electrician Exam
Five 5 kW household dryers are supplied by one feeder. What is the calculated dryer load under the NEC 2020/2023?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12030
- B: 21,250 VA
Explanation
Five dryers at 5,000 VA each give 25,000 VA (220.54 and Table 220.54). The demand factor for five dryers is 85 % in the NEC 2020/2023, so 25,000 x 0.85 = 21,250 VA.
More questions: Load Calculations
- 12031Under the NEC 2020/2023, what is the demand factor for 20 household electric dryers on one feeder?
- 12032A dwelling has one electric dryer rated 3,800 W. What load must be used for it in the NEC 2020/2023 service calculation?
- 12079Under the NEC 2020 or 2023, what is the feeder load for 3 household electric dryers rated 5,000 W each?
- 12080Under the NEC 2020 or 2023, what is the feeder load for 6 household electric dryers rated 6,000 W each?
- 12081Under the NEC 2020 or 2023, what is the feeder load for 7 household electric dryers rated 5,000 W each?
- 12083Six 12 kW ranges are on one apartment feeder. What range demand load applies under the NEC 2020 or 2023?