A three-phase 208 volt circuit of 10 AWG copper (10,380 circular mils) supplies 25 A per phase at 120 feet one way. What is the percent voltage drop?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13044
- D: 3.1 %
Explanation
VD = 1.732 x 12.9 x 25 x 120 / 10,380 = 6.46 V, and 6.46 / 208 = 3.1 %. Using the single-phase factor 2 gives 3.6 %, and dividing by 120 V instead of 208 V gives 5.4 %.